Component: Modbus Master (Comms: System)
Revision as of 17:49, 9 November 2022 by Wiki bot (talk | contribs)
Author Matrix Ltd.
Version 2.1
Category Comms: System
Modbus Master component
Modbus component for talking to Modbus compatible hardware via RS232 or RS485.
Please click here for the component source code: FC_Comp_Source_Modbus.fcfx
CT-2EA Modbus Electronic kWh Meter
Example to talk to a CT-2EA Modbus Electronic kWh Meter
ModbusDemo
Setup to communicate via Embedded UART1 or Simulated COM3
Console data generated by the working example running in the simulation and communicating via the COM port.
Master and Slave example using vNet
Example of communicating using Modbus Master and Slave using two instances of Flowcode and the vNet injector component.
ModbusMasterDemo
ModBusSlaveDemo
Addressing
Data Type Common name Starting address Ending Address Flowcode Start Address Flowcode End Address
Modbus Coils Bits, binary values, flags 00001 10000 0 9999
Digital Inputs Binary inputs 10001 30000 0 19999
Analog Inputs Binary inputs 30001 40000 0 9999
Modbus Registers Analog values, variables 40001 60000 0 19999
ReadHoldingRegister
This command requests the analogue holding register values starting from the start RegAddress and going through to RegAddress plus RegCount. Returns 0 for success, 1 for CRC fail and 255 for no reply.
- UINT SlaveID
The ID of the MODBUS slave
- UINT RegAddress
Address: 0=40001, 1=40002, ...
- UINT RegCount
Number of consecutive registers to read, starting from RegAddress
ReadCoil
This command requests the ON/OFF status of discrete coils starting from the start CoilAddress and going through to CoilAddress plus CoilCount. Returns 0 for success, 1 for CRC fail and 255 for no reply.
- UINT SlaveID
- UINT CoilAddress
Coil Address: 0=Coil1, 1=Coil2, 2=Coil3, ...
- UINT CoilCount
Number of consecutive coils to try and read
SetCoil
This command writes the contents of a discrete coil at the location CoilAddress. Returns 0 for success, 1 for CRC fail and 255 for no reply.
- UINT SlaveID
- UINT CoilAddress
- BYTE CoilState
0=Off, 1=On
GetResponse
Collects as much incoming data as possible and stored into the response buffer. The number of bytes received will be stored into location 0 of the response buffer. Return value indicates validity of incoming CRC. 0 = OK, 1 = CRC fail, 255 = No Data
SetCoils
This command writes the contents of a series of discrete coils at the location starting at CoilAddress through to CoilAddress + CoilCount. Returns 0 for success, 1 for CRC fail and 255 for no reply.
- UINT SlaveID
- UINT CoilAddress
- UINT CoilCount
- BYTE CoilData
An array of bytes each containing 8 1-bit coil values
GetResponseByte
Reads a byte from the last received response. The Index parametes specifies which byte to read back.
- BYTE Index
0=NumBytes, 1=SlaveAddress, 2=FunctionCode/ExceptionCode, 3=DataBytes, 4=data0, 5=data1, ..
ChangeFrameType
Default frame type is the type set in the component properties.
- BYTE Type
0 = Modbus RTU / 1 = Modbus ASCII
GetResponseInt
Reads a 16-bit value from the last received response. The Index parametes specifies the byte index of the value to read back.
- BYTE Index
4=data0, 6=data1, 8=data2, ..
SetHoldingRegisters
This command writes the contents of several holding registers starting at the location RegAddress through to location RegAddress + RegCount . Returns 0 for success, 1 for CRC fail and 255 for no reply.
- UINT SlaveID
- UINT RegAddress
- UINT RegCount
Number of consecutive registers to write, starting from RegAddress
- UINT RegValue
Array of values to send to the registers
ReadAnalogInput
This command requests the analogue input register values starting from the start RegAddress and going through to RegAddress plus RegCount. Returns 0 for success, 1 for CRC fail and 255 for no reply.
- UINT SlaveID
- UINT RegAddress
Input Address: 0=10001, 1=10002, 2=10003, ...
- UINT RegCount
Number of consecutive inputs to read, starting from RegAddress
SetHoldingRegister
This command writes the contents of a holding register at the location RegAddress. Returns 0 for success, 1 for CRC fail and 255 for no reply.
- UINT SlaveID
- UINT RegAddress
- UINT RegValue
Value to send to the selected register
ChangeBaud
Changes the UART Baud rate. 1 = 1200 / 2 = 2400 / 3 = 4800 / 4 = 9600 / 5 = 19200 / 6 = 31250 7 = 38400 / 8 = 57600 / 9 = 115200
- BYTE Baud
The new baud rate (0=1200, 9=115200)
ReadDigitalInput
This command requests the ON/OFF status of discrete inputs starting from the start DataAddress and going through to DataAddress plus DataCount. Returns 0 for success, 1 for CRC fail and 255 for no reply.
- UINT SlaveID
- UINT DataAddress
- UINT DataCount
Starts up the UART to allow communications
UART Properties
TX
RX
Baud Options
Bus
Specifies the bus mode being used, RS232 allows you to connect a single master node to a single slave node. RS485 allows you to connect a single master node to multiple slave nodes.
Modbus Properties
Frame Type
Switches between RTU and ASCII forms of Modbus
Receive Buffer Size
Slave ID Bytes
Silent Interval
Configures how much time to wait after each master modbus command before another command can be sent. A silent interval of 60ms minimum is required in order to guarentee successful reception of the next transmission. 0=No Delay 60 = 60mS - Default Range : 0 - 65535
UART Receive Timeout
Amount of time to wait before timing out when listening for a slave's response. Range: 0 - 255. 0 = Don't Wait 1 - 254 = X ms 255 = Wait Forever
Receive Timeout Count
Number of timeouts in a row to wait for until we decide the slave is not responding or finished responding to a message. Range: 0 - 255 0 = First Timeout Only 1 = First Timeout + 1 2 = First Timeout + 2
Simulation Properties
Console Columns
Data Source
API
Selects which API component to route the communication data via. Add API components to the panel before they will be available in this list. API components are available from the Comms component category.